GFCI resets at the outlet but still fails — what are we missing?

We keep running into the same one on HUD inspections: a GFCI outlet in a kitchen or bath that trips and resets fine at the outlet, the little test button clicks, the light comes back on — and the inspector still marks it as failed.

What we have learned to check before we call it done: press the test button, confirm power actually drops at that outlet and at every outlet downstream of it, then reset and confirm power comes back everywhere downstream too. A GFCI that only protects itself, or one wired so a downstream outlet stays live when it trips, is not doing the job. We also check that it is actually a GFCI where one is required, not a standard outlet someone swapped in, and that the cover and box are sound.

It is a five-minute check with a plug-in tester, and it has saved us from a failed inspection more than once. The outlet looking fine is not the same as the outlet working.

How do you test GFCIs on your turns — test button only, plug-in tester, or both?
 